ApplianceGuru.com: The Samurai Appliance Repair Forums > Do-It-Yourself Appliance Repair Help > Heating, Ventilation, and Air Conditioning (HVAC) > Heat pump - icing up in A/C mode |
|
| Moderated by: RegUS_PatOff, dkpd1581, applianceman18007260692 | Search Our Sites for More Info! |
|
|||||||||||||
| Heat pump - icing up in A/C mode | Rating:
|
| Author | Post |
|---|
| Posted: Sat May 6th, 2006 08:29 pm |
|
1st Post |
|
cwilkins Grasshopper
|
Greetings! I've got an approx. 20 year old GE heat pump that I'm trying to nurse along for a bit longer while I save my pennies for a replacement. It has presented me with various little challenges over the years, but I've always been able to get it humming along again at minimal or no cost. Now the evaporator (inside) coils are icing up in "cool" mode, and that's with no filter installed! Because the filters for this thing are apparently an odd size (18x25x1) and a pain to obtain, it has occasionally been run with no filter for a few days or a week. I figured maybe this bad habit caught up with me and the coils were clogged with dust, so today I vacuumed the coils and blew out whatever was left with compressed air. However, the coils are still icing up, even though I seem to have plenty of airflow. Also, it just doesn't seem to be cooling very well. The inside temp has gone from 80 to 81 since I turned it back on about a half hour ago. I mentioned my predicament to a neighbor and he suggested I might be low on freon. He also mentioned that they no longer make the stuff I need (R12?). Ouch! I don't suppose there's a simple and/or cheap solution for this? Pretty sure I still have one of those little cans of R12 kicking around somewhere from a fridge fix about 15 years ago. :-) I know I'm running on borrowed time, but I'm just not ready to plunk down $3-5k for a new heat pump. ("Not ready" as in "I don't have $3-5k sitting around.") Thanks very much for any help! -- Charlie
|
||||||||||||||
| |||||||||||||||
| Posted: Sat May 6th, 2006 11:14 pm |
|
2nd Post |
exsearsguy
|
NOT R-12! NOT R-12! You probably need a shot of R-22. GREEN CAN! NOT WHITE!Are you absolutely sure you have good airflow.Clean evaporator and fan blowing well.Are you trying to run it at night with cool outside temps.That will cause freezing up also. If you have a dirty evaporator vacuuming and compressed air won't hardly get it. And it sounds like you have a dirty evaporator. I clean mine and oil the fan motors every year myself.
|
|||||||||||||
| ||||||||||||||
| Posted: Sun May 7th, 2006 12:24 am |
|
3rd Post |
|
cwilkins Grasshopper
|
exsearsguy wrote: NOT R-12! NOT R-12! You probably need a shot of R-22. GREEN CAN! NOT WHITE!Are you absolutely sure you have good airflow.Clean evaporator and fan blowing well.Are you trying to run it at night with cool outside temps.That will cause freezing up also. If you have a dirty evaporator vacuuming and compressed air won't hardly get it. And it sounds like you have a dirty evaporator. I clean mine and oil the fan motors every year myself. Er... Oops. Well that explains why the compressor exploded through the side of the outside unit and ran down the street yelping... So I guess I need this thing sucked out and recharged now, assuming I haven't done permanent damage? It was only 14oz, so I would hope I might get off lightly for my act of stupidity. (...or am I going to fall over dead when I find out how much a couple of pounds of R22 costs these days?) Thanks for your advice exsearsguy. I only wish I'd been a little smarter and a little less impatient. Now if you'll excuse me while I go sit in the corner and suck my thumb... -cw-
|
||||||||||||||
| |||||||||||||||
| Posted: Sun May 7th, 2006 07:16 am |
|
4th Post |
exsearsguy
|
no permanent damage. If you can locate some 22 I'll explain a sweepcharge method to you.
|
|||||||||||||
| ||||||||||||||
| Posted: Sun May 7th, 2006 05:45 pm |
|
5th Post |
|
cwilkins Grasshopper
|
Thanks. That's quite a relief (though I'm still kicking myself for wasting a can of R-12...) Looks like I can get a 30lb tank of R-22 and a manifold for about $110 online. All I have to do is get my EPA certification first. So before I place an order, any thoughts about that, or other equipment I'll need to do a sweep charge? -cw-
|
||||||||||||||
| |||||||||||||||
| You have chosen to ignore ahammer48. click Here to view this post |
|---|
| Posted: Thu May 11th, 2006 07:22 am |
|
7th Post |
exsearsguy
|
Charlie a sweep charge is basically using your compressor as the vacuum pump. Hook your gauges( remember to purge your hoses) to the high and lo sides,make sure they're closed and then fire up the unit.Open the hi side and let the old junk out.When it's about empty(you can tell by the sound and pressure readings),close it up and then add some R-22, let it run a little while.Then let the new gas out.Should be pretty clean now and ready to charge. Don't let it get plumb empty when you're doing this.The refrigerant helps move the oil to the compressor and if you let it run empty you might damage your compressor.Just be careful and it 'll be ok.
|
||||||||||||||
| |||||||||||||||
| Posted: Fri May 19th, 2006 03:38 am |
|
8th Post |
|
cwilkins Grasshopper
|
[time passes...] Thanks for the info on the sweep charge, but well... I kinda went off the deep end. Luckily we've had a spell of mild weather, so I did some research and ended up ordering some stuff online. So I've got a set of gauges, a 3cfm vacuum pump and a 30lb tank of ES-22a (hydrocarbon substitute, no license required). Evacuated down to 29+ inches and left that for an hour or so. Came back and found it down around 28. Could just be some vaporization, rather than a leak, if I understand correctly. Anyhow, outside unit said it was factory charged with 5lb15oz of R-22. Not sure about the lines or the inside unit. Based on claims that 1lb of ES-22a replaces 2.5lbs of R-22, I charged with about 2lbs (according to the bathroom scale) of ES-22a for starters and turned the system on in cooling mode. Pressures stabilized at around 38psi on the low side and 135 on the high side. Outside temp was about 60F and about 75F inside, so perhaps not ideal conditions for doing this. Put in another 1/2 pound, which brought the pressures up to 40/145. According to the charts for ES-22a, that works out to around 19F/87F. The temp coming out of the vents was about 55F. So it's definitely working better than before, but I have no clue how close to the mark I am. This is where my lack of knowledge/experience really shows. Apparently to charge a system "by the book" you're supposed to take wet/dry bulb temp readings of the coils, convert your refrigerant pressures to temperatures, do a couple of calculations and home in on the correct super heat(capillary)/cool(TXV) values. Well first off, I don't know the "correct" values for my 20+ y.o. GE Weathertron or where to find them, or even if I have a TXV or not. Second, I'm under the impression that there are other ways (perhaps not as precise?) to determine correct charge. Pressures vs. ambient indoor/outdoor temp? Temp of suction line? Sounds? "Feel?" Smell?!? (I know a burning smell is bad...) Oh, the outside unit mod# is BWB736A100A1, if that's of any help. Also the ES-22a page at es-refrigerants.com has a temp/pressure chart: http://www.es-refrigerants.com/products/w/id/45/details.asp Mucho thanks for any spare clues! -cw
|
|||||||||||||
| ||||||||||||||
| Posted: Fri May 19th, 2006 03:56 am |
|
9th Post |
|
cwilkins Grasshopper
|
Thanks for the voice of reason ahammer48. I know I'm messing where I really don't belong. Yes, I should just call someone, but where's the fun in that?!? Seriously, this is all a product of (some) mechanical aptitude, insatiable curiousity and an inability to simply throw large sums of money at such problems. I was emboldened in this latest effort by success with other work on refrigeration systems, including the repair of a fridge with a hole rusted through the top of the compressor housing. Granted, the stakes are a little higher this time... -cw-
|
||||||||||||||
| |||||||||||||||
| Posted: Sun May 21st, 2006 08:10 pm |
|
10th Post |
|
cwilkins Grasshopper
|
Some new numbers here... Still a little cool outside, but not much I can do about that. Inside/Outside ambient: 74F/76F Lo/Hi Pressure: 57psi/205psi Pressures converted to temperature: 34F/112F Suction line temp at compressor: 53F (19F superheat?) Temp at nearest indoor vent: 55F I've also noticed the compressor is quieter than the fan now. It's now sounding about the same or a little less noisy than before all this happened. Total refrigerant added - about 5.5lbs of ES-22a. So now the question is "what caused all this?" 20+ years of very slow leak (bad service valve/cap?) or something less slow and more recent? The service caps on this unit are brass with no seals. I'm told they tend to be leaky, which is presumably not a good thing. When I removed the hi side cap, it gave me a little PSST, so sounds like the valve was leaking at least a tiny bit. Perhaps the question is, was the cap leaking a little too? I plan to leave the gauges hooked up for a couple of days to keep an eye on things. Might new caps be a good idea anyway, just as general preventative maintenance? Thanks for any clues... -cw-
|
|||||||||||||
| ||||||||||||||
| Posted: Mon May 22nd, 2006 03:44 am |
|
11th Post |
exsearsguy
|
Charlie, I think you'll be ok.Keep in mind that as your outside ambient goes up,so will your inside ambient.Sounds like enough refrigerant.If in doubt, just look at your suction line on a hot day.If it's sweating,it's full. CLEAN THAT EVAPORATOR!!
|
||||||||||||||
| |||||||||||||||
| Posted: Mon May 22nd, 2006 04:50 am |
|
12th Post |
|
cwilkins Grasshopper
|
The suction line was sweating today. I also noticed a little sweat inside the outdoor unit, on tubing leading to/from the filter/dryer. I'm assuming that's still suction, though I didn't trace it out. A veteran HVAC guy who's a neighbor of a coworker spent some time on the phone with me today and put up with me picking his brain for an hour or so. His final verdict seems to be that I'm possibly still a little low, but that it's hard to tell with these mild temps we're having, at least with a non-TXV system. He's sending me some kind of slide rule type superheat calculator to play with, and a couple of charts. This should be fun! I hear ya about the evaporator. Do I want the stuff you just spray on and gets rinsed off by the condensate? ...or is that just a bit too magical to actually work well? -cw- Last edited on Mon May 22nd, 2006 04:54 am by cwilkins |
|||||||||||||
| ||||||||||||||
| Posted: Mon May 22nd, 2006 05:39 am |
|
13th Post |
exsearsguy
|
I just open mine up, spray it with a generic cleanser( 409, Windex, etc.) then scrub it with a wire brush. Then I spray it with the water hose. Ta-da,it's clean.Maybe pressure wash your condenser. I think your neighbor is close on. But I'd wait on warmer temps before I did anything. Oil your fan motors while have it open. And NO 3-in 1 oil in a fan motor. Don't get excited about superheat, just make sure your suction line has iced tea sweat on a HOT day. Then you'll know it's full.
|
||||||||||||||
| |||||||||||||||
| You have chosen to ignore ahammer48. click Here to view this post |
|---|
| Posted: Sun May 28th, 2006 02:58 am |
|
15th Post |
|
applianceman18007260692 Fellow, Academy of Sublime Masters of Appliantology
|
At my store I sell a very good product call vapco FCC-1 evap coil cleaner(non-rinse) for the A coil and something called Brite-Alum for the outside unit . I suggest you go to you local HVAC supplier. use these products according to their directions
____________________ "May the hinges of our friendship never grow rusty" -old Irish saying Buy me a Beer: http://web.me.com/zenzoidman/applianceman18007260692/ |
||||||||||||||
| |||||||||||||||
| Posted: Sun May 28th, 2006 04:54 am |
|
16th Post |
exsearsguy
|
I agree that a hose won't cut it. That's why I said pressure wash. And believe me. air won't cut it either.
|
|||||||||||||
| ||||||||||||||
| Current time is 02:05 am
|
|
| ApplianceGuru.com: The Samurai Appliance Repair Forums > Do-It-Yourself Appliance Repair Help > Heating, Ventilation, and Air Conditioning (HVAC) > Heat pump - icing up in A/C mode | Top |
| Find Appliance Parts & Diagrams Here |
| Enter a model number, part number, type of appliance, brand, or even a part description. |
|
365-day return policy on all parts ordered through this site! |
FAQs | Contact | Apprenticeship | Consultations | Parts | Model Number Help | Newsletter | Beer | Fixitnow.com