York gy8s080b16dh11b problems :(  Rate Topic 
AuthorPost
 Posted: Tue Oct 5th, 2010 04:16 am
  PM Quote Reply
1st Post
delawaredrew
Master Appliantologist
 

Joined: Wed May 2nd, 2007
Location: Washington USA
Posts: 137
Flavorite Brew: Paulaner Salvator
Status: 
Offline
Hi all,
I have a York GY8SB1611DH11B furnace that is giving me problems. I work on gas appliances all the time so it seemed that I could take a stab at it.

It has been failing to ignite for several days, The ventor would run then the blower but no ignition.  I finally got under the house to check it out today. It was flashing the code for a pressure switch problem and indeed the port off the ventor was clogged with grit.  So I cleaned that out and it tried to start, even going so far as opening the valve. 

The ignitor was not connected at that point so it didn't ignite but seemed like it would have.  It went into lockout due to lack of ignition.  Being impatient I turned off the power to it for a few minutes thinking it might reset the board.  After powering it back up it blew the 3amp fuse on the board when it tried to start.

I replaced that fuse and the indicator light lit up green so I figured all was ok.  However when I turned the thermostat up it blew it again.  I replaced the fuse again, and disconnected the ignitor just to be certain it wasn't shorting it out and tried again.  It blew the fuse again.

What do you think?  I'm thinking that board has a issue like a bad relay, but it seems like a heck of a coincidence that it would fail just from being power cycled?  What exactly does the fuse protect on this? 

Thanks
Drew

Back To Top PM Quote Reply  

 Posted: Tue Oct 5th, 2010 12:41 pm
  PM Quote Reply
2nd Post
RegUS_PatOff
Fellow, Academy of Sublime Masters of Appliantology


Joined: Sat Sep 24th, 2005
Location: Milwaukee, Wisconsin USA
Posts: 16509
Flavorite Brew: Indian Head. Black & White
Status: 
Offline
this may be your manual, but I don't see a Fuse on the Board ..

I'll do some more searching...

upflow
http://yorkupg.com/PDFFiles/268893-UUM-A-0407.pdf


downflow
http://www.yorkupg.com/PDFFiles/98601-UUM-A-1104.pdf



____________________
The new repair forums==> http://appliantology.org

RegUS_PatOff http://www.youtube.com/watch?v=oPAY2LsKVEw

my video production: “Easter Seals Walk With Me” http://www.youtube.com/watch?v=-EBiLyYXMiA
Back To Top PM Quote Reply

 Posted: Wed Oct 6th, 2010 01:04 am
  PM Quote Reply
3rd Post
delawaredrew
Master Appliantologist
 

Joined: Wed May 2nd, 2007
Location: Washington USA
Posts: 137
Flavorite Brew: Paulaner Salvator
Status: 
Offline
If not exactly the same it is similar, I couldn't find a manual for it either.  The fuse is listed as #14 on the parts list, and it is vaguely shown on the board diagram but not numbered or marked at all.  It's the vertical bar on the lower left of figure #9.  It is on the control board itself.

I've been thinking about it all day but nothing new has come to me.  If I understand the sequence of ignition, the fuse blows when the board tries to turn on the ventor/combustion air fan.  I tried it with that fan disconnected and it still blew the fuse.  I've now used up all the 3a fuses the local autoshop has in stock!  I can get a new board but will be ticked if I dump $100 for a unreturnable part and it doesn't do it. 

I may have make or get a resettable jumper fuse that I can test with. I used to have a 15a one that I used for MW ovens that came in handy.
This pic I stole off ebay is a similar board, the fuse is the purple thing in lower left.


Attachment: board.JPG (Downloaded 58 times)

Last edited on Wed Oct 6th, 2010 01:15 am by delawaredrew

Back To Top PM Quote Reply  

 Posted: Wed Oct 6th, 2010 03:47 am
  PM Quote Reply
4th Post
RegUS_PatOff
Fellow, Academy of Sublime Masters of Appliantology


Joined: Sat Sep 24th, 2005
Location: Milwaukee, Wisconsin USA
Posts: 16509
Flavorite Brew: Indian Head. Black & White
Status: 
Offline
somewhere I remember reading the the 3A Fuse protects the 24v Transformer Secondary.

After looking again at the wiring diagram, the Transformer Secondary powers the House Wall Thermostat.

Disconnect the Thermostat Wiring at the Furnace (at least the Red wire)
and try again.

You could wire in an external Fuse Holder...


click on picture



____________________
The new repair forums==> http://appliantology.org

RegUS_PatOff http://www.youtube.com/watch?v=oPAY2LsKVEw

my video production: “Easter Seals Walk With Me” http://www.youtube.com/watch?v=-EBiLyYXMiA
Back To Top PM Quote Reply

 Posted: Wed Oct 6th, 2010 04:27 am
  PM Quote Reply
5th Post
delawaredrew
Master Appliantologist
 

Joined: Wed May 2nd, 2007
Location: Washington USA
Posts: 137
Flavorite Brew: Paulaner Salvator
Status: 
Offline
That makes some sense. I did disconnect the thermostat at one point. The indicator on the board did light up as normal, but it blew the fuse as soon as I wired it back in and asked it to heat. I also tried to just cross the red and white at the board, which also blew the fuse when I powered it up. I wasn't sure what to make of it or if that was a bad thing to do.

If that fuse is on the 24v circuit at least it gives me something to check. I can check that for 24v, maybe that'll tell me something. Maybe the transformer is bad on the board, which still means a new board but it would be nice to know.

It does have a heat pump style thermostat, with 2 mercury switches, and way more internal wiring than a simple gas furnace needs.

Last edited on Wed Oct 6th, 2010 04:27 am by delawaredrew

Back To Top PM Quote Reply  

 Posted: Wed Oct 6th, 2010 04:36 am
  PM Quote Reply
6th Post
RegUS_PatOff
Fellow, Academy of Sublime Masters of Appliantology


Joined: Sat Sep 24th, 2005
Location: Milwaukee, Wisconsin USA
Posts: 16509
Flavorite Brew: Indian Head. Black & White
Status: 
Offline
Transformer sounds OK

and that would be 24v AC

disconnect the Thermostat wires and do some OHM meter tests on those wires

and on the Furnace connectors.... Gas Valve

OR there's a pinched/shorted wire to the Thermsostat or on the Furnace

 



____________________
The new repair forums==> http://appliantology.org

RegUS_PatOff http://www.youtube.com/watch?v=oPAY2LsKVEw

my video production: “Easter Seals Walk With Me” http://www.youtube.com/watch?v=-EBiLyYXMiA
Back To Top PM Quote Reply

 Posted: Mon Oct 11th, 2010 03:21 am
  PM Quote Reply
7th Post
ACtechGUY
Master Appliantologist


Joined: Sun Sep 27th, 2009
Location: New Orleans, Louisiana USA
Posts: 137
Flavorite Brew: Landshark
Status: 
Offline
The problem you describe almost always comes from shored thermostat wires. Check the wiring at the low voltage terminal strip very closely. you have likely shorted the W wire to the C wire in the course of looking for your ignition problem Or You may have pinched one of the wires by sitting or standing on it.

To verify where the problem is detach ALL wires from terminal strip.
install jumper wire from W to R . If the fuse does not blow the problem is in the wires(likly right near the furnace).
If it blowes the fuse , then you have a short to ground in the furnace safty circuit. maybe a misplaced wire?

Last edited on Mon Oct 11th, 2010 03:24 am by ACtechGUY



____________________
Don't know much. But learned early on, once you let the smoke out of a something electrical, you can never put it back in!!:oops:
Back To Top PM Quote Reply  

 Posted: Mon Oct 11th, 2010 05:58 am
  PM Quote Reply
8th Post
delawaredrew
Master Appliantologist
 

Joined: Wed May 2nd, 2007
Location: Washington USA
Posts: 137
Flavorite Brew: Paulaner Salvator
Status: 
Offline
ACtechGUY wrote: The problem you describe almost always comes from shored thermostat wires. Check the wiring at the low voltage terminal strip very closely. you have likely shorted the W wire to the C wire in the course of looking for your ignition problem Or You may have pinched one of the wires by sitting or standing on it.

To verify where the problem is detach ALL wires from terminal strip.
install jumper wire from W to R . If the fuse does not blow the problem is in the wires(likly right near the furnace).
If it blowes the fuse , then you have a short to ground in the furnace safty circuit. maybe a misplaced wire?

Thanks for the advice guys, this hasn't been high on my list as it isn't cold here yet, (or ever really) but I want to get back under there and figure it out this week.

I'll check out the wiring, it runs straight up out of the unit it a wall but I may have crimped it or otherwise messed it up while wriggling around under there.  It blew the fuse before I had any reason to be in the blower compartment where the control is, I did have the ignitor out already, so maybe I did something in that area.

Would a bad pressure switch cause an issue like this?  When I pulled the hose off to clear it out the hose was attached far more firmly to the pressure switch than I expected and required a bit or persuasion to slide off, maybe I damaged the diaphragm or something, or shorted a wire there.

Just so I am clear as to what the 24v circuit is doing:  does the board put 24v out on the W or R?  I assume one sends 24v up and the other returns?

Last edited on Mon Oct 11th, 2010 06:00 am by delawaredrew

Back To Top PM Quote Reply

 Posted: Wed Oct 13th, 2010 04:21 am
  PM Quote Reply
9th Post
ACtechGUY
Master Appliantologist


Joined: Sun Sep 27th, 2009
Location: New Orleans, Louisiana USA
Posts: 137
Flavorite Brew: Landshark
Status: 
Offline
The pressure switch is not an issue unless one of the wires is touching the metal of the unit or pressure switch. The pressure switch is just that( a switch) if the wires touch together the worst that will happen is the furnace will not fire.

You can measure 24 volts AC between R and C at the board. the 24 volts "hot" side of the transformer is "R" . The R terminal feeds the themostat. The thermostat then switches back differnt 24 volt outputs depending on the mode and what the stat is calling for.
R= 24 volts to thermostat
G= thermostat 24 v output to furnace to turn on fan
W= thermostat 24 v output to furnace to turn on heat
Y= thermostat 24 v output to furnace and condensiong unit to turn on cooling
All these readings are to the "C" terminal
R to C =24 volts AC
G to C "
Y to C "
W to C "

When you disconnected the ignitor , maybe you plugged back ta wrong wire that you knocked loose near the ignitor?

Last edited on Wed Oct 13th, 2010 04:26 am by ACtechGUY



____________________
Don't know much. But learned early on, once you let the smoke out of a something electrical, you can never put it back in!!:oops:
Back To Top PM Quote Reply  

 Posted: Wed Oct 13th, 2010 04:32 am
  PM Quote Reply
10th Post
RegUS_PatOff
Fellow, Academy of Sublime Masters of Appliantology


Joined: Sat Sep 24th, 2005
Location: Milwaukee, Wisconsin USA
Posts: 16509
Flavorite Brew: Indian Head. Black & White
Status: 
Offline
delawaredrew wrote: .. does the board put 24v out on the W or R?  I assume one sends 24v up and the other returns?

as shown on the wiring diagram posted,

the 24v AC goes out the Red wire to the thermostat, and returns on the White wire.

It could also come back on the Green (Fan ON)

and Yellow (COOLING)

it shouldn't be connected or touching the C terminal



____________________
The new repair forums==> http://appliantology.org

RegUS_PatOff http://www.youtube.com/watch?v=oPAY2LsKVEw

my video production: “Easter Seals Walk With Me” http://www.youtube.com/watch?v=-EBiLyYXMiA
Back To Top PM Quote Reply

 Posted: Wed Oct 13th, 2010 06:07 am
  PM Quote Reply
11th Post
delawaredrew
Master Appliantologist
 

Joined: Wed May 2nd, 2007
Location: Washington USA
Posts: 137
Flavorite Brew: Paulaner Salvator
Status: 
Offline
Thanks.  Only R and W here.  That does explain why the fan only switch never worked too.

Still trying to find time to go down there and see what I can find out;  after I replace the starter in my truck and take care of my gf who just broke her arm and needs surgery... what a freakin' week so far!

Back To Top PM Quote Reply  

 Posted: Wed Oct 13th, 2010 01:13 pm
  PM Quote Reply
12th Post
RegUS_PatOff
Fellow, Academy of Sublime Masters of Appliantology


Joined: Sat Sep 24th, 2005
Location: Milwaukee, Wisconsin USA
Posts: 16509
Flavorite Brew: Indian Head. Black & White
Status: 
Offline
If it only uses Red and White
(heat only, no cooling, no Fan control)

then IF there was a short across Red to White, it wouldn't blow the Fuse,
it would just turn the heat on continuously.

Unless either of those wires was shorted to ground.

 
Disconnect all of the external Thermostat wires form the Furnace Terminal Strip,
while making sure neither wire is shorted/pinched to chassis (ground)
and also, not touching the C terminal

 

 



____________________
The new repair forums==> http://appliantology.org

RegUS_PatOff http://www.youtube.com/watch?v=oPAY2LsKVEw

my video production: “Easter Seals Walk With Me” http://www.youtube.com/watch?v=-EBiLyYXMiA
Back To Top PM Quote Reply

 Posted: Mon Oct 18th, 2010 01:27 am
  PM Quote Reply
13th Post
delawaredrew
Master Appliantologist
 

Joined: Wed May 2nd, 2007
Location: Washington USA
Posts: 137
Flavorite Brew: Paulaner Salvator
Status: 
Offline
Hi guys,
Good and bad news on the furnace.  The good news is that it is running as I type this, heating normally so far.  The bad news is I have no idea what I did to fix it!

I went under the house with all tools and meters and all, all the stuff I use to do appliances; expecting to be cursing loudly and very puzzled before long.  I can't curse at work so I tend to get it all out during work around the house.

Before reapplying power I checked out all 3 TCOs, the ventor motor, gas valve, anything that I could get my probes on.  Everything seemed to check as expected.  The pressure switch was a little bit of a puzzle, as I could hear air escaping as I blew into it's hose.  The hose is fine but the switch definitely allows air to pass through it. Not something I expect from the type of water level/pressure switches I see on washers so I wasn't sure what to make of that.

So... I disconnected the 2 thermo wires replaced the 3a fuse and  got a nice slowly flashing green light.  The Red wire is carrying 27v, White has continuity to ground, both on the board and after it passes from the unit.  again that puzzed me but I went ahead and crossed them and, voila!!!!  It started right up, previously that had blown the fuse?  WTF?

I reconnected the thermo, had my gf turn it on inside and it started back up as normal.  It has just turned off, at the set point.  Wish I knew what I did but I'll take results over skill on this one!

Thanks for the advice!





Back To Top PM Quote Reply  

 Posted: Mon Oct 18th, 2010 10:42 am
  PM Quote Reply
14th Post
Budget Appliance Repair
Fellow, Academy of Sublime Masters of Appliantology
 

Joined: Sat Apr 2nd, 2005
Location: Eureka, California USA
Posts: 2870
Flavorite Brew: 
Status: 
Offline
As far as the pressure switch leaking air when you are blowing into it, that is normal.

There is a very small air bleed hole at the base of the hose attachment stub, I believe it is to keep from putting to much pressure on the switch diaphragm.



____________________
William Burk (Willie)
Willie's Budget Appliance Repair
Eureka, CA 95501
Back To Top PM Quote Reply

 Posted: Mon Oct 18th, 2010 06:13 pm
  PM Quote Reply
15th Post
delawaredrew
Master Appliantologist
 

Joined: Wed May 2nd, 2007
Location: Washington USA
Posts: 137
Flavorite Brew: Paulaner Salvator
Status: 
Offline
Thanks budget, I was curious about that.  I figured it must be like you said instead of the switch having a leak or the control wouldn't read enough combustion airflow to start. 
Any thoughts on the 27v output to the thermostat?  Spec is 24v I hear.  10-15% over voltage seems a little much for a healthy transformer.

Back To Top PM Quote Reply  

 Posted: Tue Oct 19th, 2010 12:06 pm
  PM Quote Reply
16th Post
Budget Appliance Repair
Fellow, Academy of Sublime Masters of Appliantology
 

Joined: Sat Apr 2nd, 2005
Location: Eureka, California USA
Posts: 2870
Flavorite Brew: 
Status: 
Offline
delawaredrew wrote: Any thoughts on the 27v output to the thermostat?  Spec is 24v I hear.  10-15% over voltage seems a little much for a healthy transformer.

Is the 27 volt reading without the load attached?   Even if with load attached it's not uncommon to see secondary side of a 24 volt rated transformer putting out anything between 24 and 28 volts.



____________________
William Burk (Willie)
Willie's Budget Appliance Repair
Eureka, CA 95501
Back To Top PM Quote Reply

 Posted: Tue Oct 19th, 2010 02:36 pm
  PM Quote Reply
17th Post
delawaredrew
Master Appliantologist
 

Joined: Wed May 2nd, 2007
Location: Washington USA
Posts: 137
Flavorite Brew: Paulaner Salvator
Status: 
Offline
Yeah 27v with no load, nothing connected.
It has been fine so far so whatever I did I must have done correctly.
Thanks for the help, the voltage was a lingering ? so if that isn't odd I am happy with the furnace.

Back To Top PM Quote Reply  

 Posted: Wed Oct 20th, 2010 02:43 am
  PM Quote Reply
18th Post
JJDH

 

Joined: Fri Aug 27th, 2010
Location: Ohio USA
Posts: 43
Flavorite Brew: bud
Status: 
Offline
Budget Appliance Repair wrote: As far as the pressure switch leaking air when you are blowing into it, that is normal.

There is a very small air bleed hole at the base of the hose attachment stub, I believe it is to keep from putting to much pressure on the switch diaphragm.

Little hole is a moisture vent.



____________________
Model sears kenmore 41744052400
Back To Top PM Quote Reply

 Posted: Sun Oct 24th, 2010 04:37 pm
  PM Quote Reply
19th Post
ACtechGUY
Master Appliantologist


Joined: Sun Sep 27th, 2009
Location: New Orleans, Louisiana USA
Posts: 137
Flavorite Brew: Landshark
Status: 
Offline
Regarding the diapham...... it DOES NOT work on positive pressure . It senses Vacume. The way to verify a diapham and it's switch are functioning is to suck on the tube, not blow in it. You are probably lucky you didn't damage the diapham by blowing into it:shock:.

About the 27 volts. Transformer output voltage is a direct result of input voltage and the load on the transformer. You probably have a high 120 volt input. If you have 115 volt in you might get 24 volts out. if you have 125 volts in you might get a higher volt out like 27 volts. Also if you had componets actively powered by the transformer you would see a lower voltage.

Your furnace will likely work just fine now... you probably shifted that shorted to ground connector or wire back into the correct position when you checked all your devices.

Your original problem sounds like it WAS related to the pressure switch being clogged , You might just be ok now.

Last edited on Sun Oct 24th, 2010 04:42 pm by ACtechGUY



____________________
Don't know much. But learned early on, once you let the smoke out of a something electrical, you can never put it back in!!:oops:
Back To Top PM Quote Reply  

 Posted: Sun Oct 24th, 2010 08:57 pm
  PM Quote Reply
20th Post
delawaredrew
Master Appliantologist
 

Joined: Wed May 2nd, 2007
Location: Washington USA
Posts: 137
Flavorite Brew: Paulaner Salvator
Status: 
Offline
Thanks for the voltage info.

The info about the pressure switch answers a few questions, as it enters the ventor fan housing behind its blades. I had wondered how it built up enough pressure to affect the switch in that position.

I learned the hard way on a washer years ago about being gentle with diaphragm switches so I didn't apply much force by mouth, the drain or bleed hole must have saved me from my ignorance.

It is working fine now, but I would like to know what caused the fuse to blow repeatedly. I'm guessing there is a short somewhere in the short section of thermo wire leading out of the unit, nothing that I can see there but maybe it is under the insulation and shorting to one of the unused colors.

Back To Top PM Quote Reply

Current time is 10:35 pm Tell a friend about this page... all your other friends are doing it!  
ApplianceGuru.com: The Samurai Appliance Repair Forums > Do-It-Yourself Appliance Repair Help > Heating, Ventilation, and Air Conditioning (HVAC) > York gy8s080b16dh11b problems :( Top



Find Appliance Parts & Diagrams Here
Enter a model number, part number, type of appliance, brand, or even a part description.

365-day return policy on all parts ordered through this site!

FAQs | Contact | Apprenticeship | Consultations | Parts | Model Number Help | Newsletter | Beer | Fixitnow.com

Your Sometimes-Lucid Host:
ApplianceGuru.com:  The Samurai Appliance Repair Forums Home
"If I can't help you fix your appliance and make you 100% satisfied, I will come to your home and slice open my belly, spilling my steaming entrails onto your floor."


UltraBB 1.17 Copyright © 2007-2008 Data 1 Systems
Page processed in 0.9330 seconds (14% database + 86% PHP). 30 queries executed.

Web Analytics