AC Compressor wont kick on  Rate Topic 
AuthorPost
 Posted: Mon Aug 30th, 2010 10:17 pm
  PM Quote Reply
1st Post
Jaks69
Senior Apprentice Appliantologist
 

Joined: Mon Jun 18th, 2007
Location: Illinois USA
Posts: 33
Flavorite Brew: Miller Lite
Status: 
Offline
I went upstairs last night to a nice warm room. I checked the air and I see the compressor is not kicking on (8 years old) I have yet to check, but from what i understand if you ohm out the cap and it reads zero the cap is dead. When I turn on the air the contactor pulls in and the fan turns on in the furnace and on the compressor outside. What can i check on the compressor to determine if it is good?

 

Up until last night, this unit has worked flawless.   

Back To Top PM Quote Reply  

 Posted: Tue Aug 31st, 2010 12:43 am
  PM Quote Reply
2nd Post
JJDH

 

Joined: Fri Aug 27th, 2010
Location: Ohio USA
Posts: 43
Flavorite Brew: bud
Status: 
Offline
Take an amp draw on compressor common see if its running. Second, the line outside, the smaaler line is liquid, is it warm, is the bigger line the vapor, beer can cold inside where it enters the duct work?. Get the temp split.  Those will tell u if the compressor is running. Is ur filter clean? Are the coils inside and outside clean. Do you have 240 volts at disconnect. Is there 110 on each leg? this could get very complicated very fast. Is there continuity to ground. Do you have guages? What aire your air temps in going and outgoing? what is the condenser air entering temp? What is the return air wet bulb temp? Piston or txv? What is the model and serial?

Last edited on Tue Aug 31st, 2010 12:46 am by JJDH



____________________
Model sears kenmore 41744052400
Back To Top PM Quote Reply

 Posted: Tue Aug 31st, 2010 02:19 pm
  PM Quote Reply
3rd Post
Jaks69
Senior Apprentice Appliantologist
 

Joined: Mon Jun 18th, 2007
Location: Illinois USA
Posts: 33
Flavorite Brew: Miller Lite
Status: 
Offline
I ohm'd out the cap and the compressor side was Zero, I borrowed a cap from another unit plugged it in and the compressor started. I found the problem (bad capacitor) now I have to figure out what size it is, there is no writing on it. It is a Dual Run, Fan and compressor.

Back To Top PM Quote Reply  

 Posted: Wed Sep 1st, 2010 01:19 am
  PM Quote Reply
4th Post
AmTec Services



Joined: Sun May 16th, 2010
Location: Tampa, Florida USA
Posts: 93
Flavorite Brew: Budwieser
Status: 
Offline
What make and model? I might be able to help.

.....................AmTec;)



____________________
The futures so bright, I gotta wear shades!
Back To Top PM Quote Reply

 Posted: Wed Sep 1st, 2010 03:53 am
  PM Quote Reply
5th Post
JJDH

 

Joined: Fri Aug 27th, 2010
Location: Ohio USA
Posts: 43
Flavorite Brew: bud
Status: 
Offline
DONT run it with the wrong size cap



____________________
Model sears kenmore 41744052400
Back To Top PM Quote Reply  

 Posted: Wed Sep 1st, 2010 06:13 pm
  PM Quote Reply
6th Post
applianceman18007260692
Fellow, Academy of Sublime Masters of Appliantology


Joined: Thu Nov 17th, 2005
Location: Mobile, Alabama USA
Posts: 1119
Flavorite Brew: Keystone Light
Status: 
Offline
Get a HS650 torque multiplier and add it onto your existing cap. 
You can piggyback it on your existing cap and not have to worry about installing the wrong capacitor. What you do is connect it to HERM and Common. It will assist the older cap.



____________________
"May the hinges of our friendship never grow rusty"
-old Irish saying

Buy me a Beer: http://web.me.com/zenzoidman/applianceman18007260692/
Back To Top PM Quote Reply

 Posted: Wed Sep 1st, 2010 06:44 pm
  PM Quote Reply
7th Post
RegUS_PatOff
Fellow, Academy of Sublime Masters of Appliantology


Joined: Sat Sep 24th, 2005
Location: Milwaukee, Wisconsin USA
Posts: 16509
Flavorite Brew: Indian Head. Black & White
Status: 
Offline
Jaks69 wrote:
I ohm'd out the cap and the compressor side was Zero ...
 

applianceman18007260692 wrote: 
Get a HS650 torque multiplier and add it onto your existing cap. 
You can piggyback it on your existing cap and not have to worry about installing the wrong capacitor. What you do is connect it to HERM and Common. It will assist the older cap.

old Cap was shorted ...



____________________
The new repair forums==> http://appliantology.org
Back To Top PM Quote Reply  

 Posted: Wed Sep 1st, 2010 07:53 pm
  PM Quote Reply
8th Post
applianceman18007260692
Fellow, Academy of Sublime Masters of Appliantology


Joined: Thu Nov 17th, 2005
Location: Mobile, Alabama USA
Posts: 1119
Flavorite Brew: Keystone Light
Status: 
Offline
OK I thought he said he was getting 0 reading. Oopz.

I am just an analog old fart in a digital world.



____________________
"May the hinges of our friendship never grow rusty"
-old Irish saying

Buy me a Beer: http://web.me.com/zenzoidman/applianceman18007260692/
Back To Top PM Quote Reply

 Posted: Thu Sep 2nd, 2010 03:45 am
  PM Quote Reply
9th Post
ACtechGUY
Master Appliantologist


Joined: Sun Sep 27th, 2009
Location: New Orleans, Louisiana USA
Posts: 137
Flavorite Brew: Landshark
Status: 
Offline
applianceman, I hate to throw firewater at you , But your recent posts regarding capacitors have been way off.

Lets assume you have a Run capacitor that is either totally failed(open circuit) or just a very low microfarad rating(incorrect cap for motor).
If you were to install a start capacitor and relay(commonly called a start kit) you almost certainly could start that motor.BUT!!!!
Start capacitors are only in the circuit for moments to seconds( depending on how long it takes the motor to come up to full speed. ) If you have the incorrect size capacitor , " a hard start " kit WILL start a compressor, BUT seeing as the start capacitor drops out of the circuit after several seconds, You now have a motor that is running with little or no POWER FACTOR CORRECTION (provided by a correct run capactior). This results in a motor that draws way too much amperage, causing motor overheating(BURNOUT), and a boatload of other things that damage a motor and its surroundings.

To sum up , NO you cannot just throw on a hard start kit to compensate for a incorrect run capacitor. That would result in premature motor failure... (like within several days to weeks)



____________________
Don't know much. But learned early on, once you let the smoke out of a something electrical, you can never put it back in!!:oops:
Back To Top PM Quote Reply  

 Posted: Thu Sep 2nd, 2010 04:07 am
  PM Quote Reply
10th Post
applianceman18007260692
Fellow, Academy of Sublime Masters of Appliantology


Joined: Thu Nov 17th, 2005
Location: Mobile, Alabama USA
Posts: 1119
Flavorite Brew: Keystone Light
Status: 
Offline
Well a hard start is simply an option to boost an existing capacitor which IS the correct one for the system, provided it ain't shorted. If they were not worth the effort would they still be on the market? I have had one mounted on my 3 ton miller unit here at the house since 2002.



____________________
"May the hinges of our friendship never grow rusty"
-old Irish saying

Buy me a Beer: http://web.me.com/zenzoidman/applianceman18007260692/
Back To Top PM Quote Reply

 Posted: Thu Sep 2nd, 2010 11:33 am
  PM Quote Reply
11th Post
AmTec Services



Joined: Sun May 16th, 2010
Location: Tampa, Florida USA
Posts: 93
Flavorite Brew: Budwieser
Status: 
Offline
With all due respect to the masters. The hard start kits only function is to give the compressor a kick in the butt on start up. It drops the start cap out of the circuit after tenths of a second. The compressor now runs with only the run cap in the circuit between run and start windings providing a phase shift in the voltage. This increases the running efficency of the PSC motor. With a bad or weak run capacitor, the motor will over heat, and eventually fail.

A little trick for you all. If you cant read the numbers on the cap, use a black perm. maker to cover the number area. Wipe off the maker with a clean paper towel. The faded numbers will hold some of the marker allowing you to read the numbers. Dosen work every time, but has helped in the past.

Hope this helps!

.....................AmTec:D



____________________
The futures so bright, I gotta wear shades!
Back To Top PM Quote Reply  

 Posted: Thu Sep 2nd, 2010 10:03 pm
  PM Quote Reply
12th Post
JJDH

 

Joined: Fri Aug 27th, 2010
Location: Ohio USA
Posts: 43
Flavorite Brew: bud
Status: 
Offline
There are 3 types of start kits. A start thermistor (PTC) (a ptc/ relay or super boost), good for a start once every 5 minuts and a HSK which is a large mfd cap with a potential 521 relay. The 521 is the best option. The booster is ok but can only provide assist when its cool,. The proper way to check a cap is a capacitence test (read the micfofarads). A capacitor has bimetal similar to a fuse underneath the terminals. Too much heat and or heat and cool repeatedly will cause it to disconnect the terminals and pop its top to protect things. The dual run capacitor balances out the motor force simulating a 3 phase circuit for the motor or compressor to run. Each compressor or motor needs the right value cap it was designed for so you dont over amp or overheat the motor or compressor. In high efficiency scroll compressors you dont always need a start kit. If the metering device is non bleed and the juice is r410a then a start kit is more necessary. A failed capacitor needs further diagnosis to ensure the compressor or motor arent what cause the failure. The dielectric fluid in a capacitor is to insulate it and keep it cool. Od pcb caps lasted forever because the fluid was better, however it was a pollutant. There are some basics. Just my 2 cents Thanks

Last edited on Thu Sep 2nd, 2010 10:05 pm by JJDH



____________________
Model sears kenmore 41744052400
Back To Top PM Quote Reply

 Posted: Fri Sep 3rd, 2010 03:27 am
  PM Quote Reply
13th Post
ACtechGUY
Master Appliantologist


Joined: Sun Sep 27th, 2009
Location: New Orleans, Louisiana USA
Posts: 137
Flavorite Brew: Landshark
Status: 
Offline
Well said JJDH,
Maybe we should compile all this good capacitor info and maybe get someone to make it a sticky. After all , something like 60% of my service calls these days are related to failed capacitors. (by the way does anyone know a brand/label/line of capacitors that will last more than 2 years?? I only use 440v rated caps and that that does not seem to help)

----Regarding start kits on scroll compressors.... Early scroll compressors did NOT like start kits put on them unless they came from the factory with a start kit. If a "kickstart" was added they would often not start reliably or just cause the start capicitor to EXPLODE(literally) after several months. I do love a good explosion from time to time.
:fart:



____________________
Don't know much. But learned early on, once you let the smoke out of a something electrical, you can never put it back in!!:oops:
Back To Top PM Quote Reply  

 Posted: Fri Sep 3rd, 2010 03:52 am
  PM Quote Reply
14th Post
applianceman18007260692
Fellow, Academy of Sublime Masters of Appliantology


Joined: Thu Nov 17th, 2005
Location: Mobile, Alabama USA
Posts: 1119
Flavorite Brew: Keystone Light
Status: 
Offline
You guys are awesome.



____________________
"May the hinges of our friendship never grow rusty"
-old Irish saying

Buy me a Beer: http://web.me.com/zenzoidman/applianceman18007260692/
Back To Top PM Quote Reply

 Posted: Fri Sep 3rd, 2010 12:17 pm
  PM Quote Reply
15th Post
AmTec Services



Joined: Sun May 16th, 2010
Location: Tampa, Florida USA
Posts: 93
Flavorite Brew: Budwieser
Status: 
Offline
Been hearing good things about Amrad caps. I've installed a few as a test. I have the same problem with caps failing. But it is a good source of income!!!:shock:

......................AmTec



____________________
The futures so bright, I gotta wear shades!
Back To Top PM Quote Reply  

 Posted: Fri Sep 3rd, 2010 12:28 pm
  PM Quote Reply
16th Post
JJDH

 

Joined: Fri Aug 27th, 2010
Location: Ohio USA
Posts: 43
Flavorite Brew: bud
Status: 
Offline
Job security.....lol. We use mars caps. when We tune up a/c units the wiring gets new connections and all components are checked, if anyhthing is wearing out we recommend new parts. I have only seen a couple of new caps fail this season.



____________________
Model sears kenmore 41744052400
Back To Top PM Quote Reply

 Posted: Sat Sep 4th, 2010 04:23 pm
  PM Quote Reply
17th Post
ACtechGUY
Master Appliantologist


Joined: Sun Sep 27th, 2009
Location: New Orleans, Louisiana USA
Posts: 137
Flavorite Brew: Landshark
Status: 
Offline
I am beginning to suspect capacitor failure is related to the high heat we have been having lately. I have easily replaced over 40 capacitors this summer.
Many failures seem to coincide with a spike in Temperature outside. Seems the caps with wax inside vs oil filled are more likely to fail in high temps. But I have seen many oil filled failed as well.

I have been training a green tech, straight out of trade school. Up until 2 weeks ago he believed the only thing that ever went wrong with a/c's was a failed capacitor. Seriously , something like 2 out of 4 calls a day is a failed cap around here.

I do not do "PREVENTIVE" parts changing. I have seen WAY to many 30 year old contactors. I have found the quality of replacement contactors and capacitors to be often not as good as the original parts in the units. I know that a cap built 8 or more years ago has a better chance of not failing vs a brand new capicitor. I am not doing my customer any favors by replacing their "OLD" part with a shiny new part that will crap out in a year.



____________________
Don't know much. But learned early on, once you let the smoke out of a something electrical, you can never put it back in!!:oops:
Back To Top PM Quote Reply  

 Posted: Sat Sep 4th, 2010 07:56 pm
  PM Quote Reply
18th Post
AmTec Services



Joined: Sun May 16th, 2010
Location: Tampa, Florida USA
Posts: 93
Flavorite Brew: Budwieser
Status: 
Offline
Agree on all counts!!!

......................AmTec:yikes:



____________________
The futures so bright, I gotta wear shades!
Back To Top PM Quote Reply

 Posted: Sun Sep 5th, 2010 06:26 pm
  PM Quote Reply
19th Post
JJDH

 

Joined: Fri Aug 27th, 2010
Location: Ohio USA
Posts: 43
Flavorite Brew: bud
Status: 
Offline
Each company has their own practices. When we do a tune up we test each component. Anything that is out of spec... we offer replacement to prevent breakdown. When contactors are fried and have a voltage drop, they get replaced with a quality part. Todays caps arent like those old grey monster pcb that lasted 30 years, besides when someone has a 30 yr old unit, it is so inefficient and outdated replacement or upgrade should be considered.



____________________
Model sears kenmore 41744052400
Back To Top PM Quote Reply  

Current time is 08:41 am Tell a friend about this page... all your other friends are doing it!  
- > Do-It-Yourself Appliance Repair Help > Heating, Ventilation, and Air Conditioning (HVAC) > AC Compressor wont kick on Top



Find Appliance Parts & Diagrams Here
Enter a model number, part number, type of appliance, brand, or even a part description.

365-day return policy on all parts ordered through this site!

FAQs | Contact | Apprenticeship | Parts | Model Number Help | Newsletter | Beer

Your Sometimes-Lucid Host:
- Home
"If I can't help you fix your appliance and make you 100% satisfied, I will come to your home and slice open my belly, spilling my steaming entrails onto your floor."


UltraBB 1.17 Copyright © 2007-2008 Data 1 Systems
Page processed in 0.1405 seconds (8% database + 92% PHP). 26 queries executed.

Web Analytics