| subzero refrigerator 561 cold at bottom warm at top | Rate Topic |
| Author | Post |
|---|
| Posted: Wed Jul 28th, 2010 10:50 pm |
|
41st Post |
|
DaveDr Grasshopper
|
I'm having a similar recurring problem with a 561. Six years ago, the evaporator was replaced. I don't think it was leaking, but I was told that "the original evaporators were prone to icing". After the evap replacement, still wouldn't cool. A second tech came out and said the fan wasn't set to the right elevation. Should be 1 1/4" down. He reset the fan and things worked well for years. Now it isn't cooling anymore. I opened up as described in the above posts and observed the following. 1) looks like the fan may be 1/16" low. How do I loosen clamp on shaft to adjust? 2) The green wire is not attached to the temp controller. 3) there are two capillaries coming from the temp controller that seem to be placed differently than in the earlier photos. One capillary has a large metal bulb near the end that is clamped below the bottom of the evaporator. The other capillary has a thin end. It is protruding about 3-4 inches below the evaporator and was caked in ice. 4) The top half of the evaporator is caked with frost/ice uniformly from right to left. Any suggestions? Can post photos if helpful.
|
||||||||||||||
| |||||||||||||||
| Posted: Wed Jul 28th, 2010 11:09 pm |
|
42nd Post |
|
RegUS_PatOff Fellow, Academy of Sublime Masters of Appliantology
|
DaveDr wrote: 4) The top half of the evaporator is caked with frost/ice uniformly from right to left. sounds like a leak, somewhere .. yes, post photo
____________________ The new repair forums==> http://appliantology.org RegUS_PatOff http://www.youtube.com/watch?v=oPAY2LsKVEw my video production: “Easter Seals Walk With Me” http://www.youtube.com/watch?v=-EBiLyYXMiA |
|||||||||||||
| ||||||||||||||
| Posted: Wed Jul 28th, 2010 11:21 pm |
|
43rd Post |
|
DaveDr Grasshopper
|
Here is the photo Attachment: Iced evaporator.jpg (Downloaded 45 times)
|
||||||||||||||
| |||||||||||||||
| Posted: Thu Jul 29th, 2010 01:02 am |
|
44th Post |
|
RegUS_PatOff Fellow, Academy of Sublime Masters of Appliantology
|
looks like a leak ... defrost it with Hair Dryer and let the Compessor run for a hour or two.. The entire Evapoprator should be slightly, evenly, completely, frosted ..
____________________ The new repair forums==> http://appliantology.org RegUS_PatOff http://www.youtube.com/watch?v=oPAY2LsKVEw my video production: “Easter Seals Walk With Me” http://www.youtube.com/watch?v=-EBiLyYXMiA |
|||||||||||||
| ||||||||||||||
| Posted: Thu Jul 29th, 2010 01:28 am |
|
45th Post |
|
DaveDr Grasshopper
|
I defrosted and adjusted the fan position on the shaft per spec. Ran it over an hour with a setting of 5 (which used to be sufficient). Had only cooled to 58 degrees. Popped it open again and no frost has formed on the evaporator yet. Fan seems to be blowing well. Will check again once it is down to temp.
|
||||||||||||||
| |||||||||||||||
| Posted: Fri Jul 30th, 2010 12:08 am |
|
46th Post |
|
DaveDr Grasshopper
|
Here is a photo after running a day. If this indicates a leak, what are next steps? Evaporator was replaced in 2004. Attachment: Evaporator After one day.jpg (Downloaded 24 times)
|
|||||||||||||
| ||||||||||||||
| Posted: Fri Jul 30th, 2010 01:00 am |
|
47th Post |
|
RegUS_PatOff Fellow, Academy of Sublime Masters of Appliantology
|
must be a leak somewhere ... was it the Fridge Evaporator that was replaced last time ?
____________________ The new repair forums==> http://appliantology.org RegUS_PatOff http://www.youtube.com/watch?v=oPAY2LsKVEw my video production: “Easter Seals Walk With Me” http://www.youtube.com/watch?v=-EBiLyYXMiA |
||||||||||||||
| |||||||||||||||
| Posted: Fri Jul 30th, 2010 01:42 am |
|
48th Post |
|
DaveDr Grasshopper
|
Yes, the Fridge evaporator and temp control unit were replaced due to icing in 2004. I believe the freon charge was fine at the time, but the new style evaporator is supposed to resist icing relative to the original equipment. "must be a leak somewhere". Are you saying that this ice pattern is consistent with low refrigerant charge?
|
|||||||||||||
| ||||||||||||||
| Posted: Fri Jul 30th, 2010 02:40 am |
|
49th Post |
|
RegUS_PatOff Fellow, Academy of Sublime Masters of Appliantology
|
yes, Evaporator was replaced, but didn't have the same (frost pattern) symptom you have now ? ... did you see him replace the Evaporator ?
____________________ The new repair forums==> http://appliantology.org RegUS_PatOff http://www.youtube.com/watch?v=oPAY2LsKVEw my video production: “Easter Seals Walk With Me” http://www.youtube.com/watch?v=-EBiLyYXMiA |
||||||||||||||
| |||||||||||||||
| Posted: Fri Jul 30th, 2010 02:45 am |
|
50th Post |
|
micgla Master Appliantologist
|
Def. looks low on freon. I'd have it checked by a professional. By the looks of the evap, looks like the original style evap to me. Newer evaps you have to crimp the cold control probes to the back of the evap coil. Leak could be anywhere...most likely evap but no way to tell unless you have it checked with leak detector or get lucky with bubbles. Run your finger over the drain trough below the evap coil (where the water drips in to the trough) do you see traces of any oil? If so, good indicator of leaky evap coil.... Last edited on Fri Jul 30th, 2010 02:47 am by micgla ____________________ I Don't know yet! |
|||||||||||||
| ||||||||||||||
| Posted: Fri Jul 30th, 2010 04:31 am |
|
51st Post |
|
DaveDr Grasshopper
|
No signs of oil in the trough below the evap. This is fishy. I didn't "see" the evaporator replaced, but I was charged $100 parts and $250 labor. I also wasn't involved in the diagnosis. I don't know if they rechecked ice pattern after initial defrost with the old evap. I assumed there was some other way to detect if freon was low. They never said the old evaporator was leaking. They said there was a "known problem" with the old design, so I needed the "new" design. In another 561 icing thread, SELFINC posted the following back in 2006: "The problem with 90% of these I find & by the way, I am an authorized Sub Zero Servicer...... The evaporator is the problem. Made of copper & the replacement from a new vendor is not copper. Sub Zero is well aware of the problem. You most likely have an ice ball on the top left corner of the evap that grows out in to the refer compartment & then falls off. I learned the hard way that changing the drier & recharging only lasts 6 months to a year & then it re-occurs. You will need to replace the evaporator & make sure your part supplier is selling you new stock & not old, you dont want to put in another copper evap." I read elsewhere that the evaporators that need to be crimped on the back are made of aluminum. The current part looks black in pictures I've seen. Including the pics earlier in this thread. The U-bends on my evaporator look like copper. I don't understand why the earlier generation evaporators had more of a problem. Is a copper evap more likely to leak or some other problem? Did the aluminum evap become available after April 2004 when my work was done? Have there been three styles of evap since 1988? Was my copper evap replaced with a new copper evap from old stock (so I really only got an expensive refrigerant recharge)? etc....
|
||||||||||||||
| |||||||||||||||
| Posted: Fri Jul 30th, 2010 02:31 pm |
|
52nd Post |
|
RegUS_PatOff Fellow, Academy of Sublime Masters of Appliantology
|
DaveDr wrote: ... This is fishy. I didn't "see" the evaporator replaced, but I was charged $100 parts and $250 labor. ... They never said the old evaporator was leaking. They said there was a "known problem" with the old design, so I needed the "new" design.... Thre Evaporator is about $ 100, Was there any part names or part numbers listed in the replacement "list" ?
____________________ The new repair forums==> http://appliantology.org RegUS_PatOff http://www.youtube.com/watch?v=oPAY2LsKVEw my video production: “Easter Seals Walk With Me” http://www.youtube.com/watch?v=-EBiLyYXMiA |
|||||||||||||
| ||||||||||||||
| Posted: Fri Jul 30th, 2010 02:37 pm |
|
53rd Post |
|
micgla Master Appliantologist
|
DaveDr wrote: No signs of oil in the trough below the evap. I would def. suggest calling a professional service company out to check your frig. Not sure when they came out with the aluminum evaps as service replacements but its been at least some years. I believe only 2 different evaps since 88. Couldn't answer if your evap was old stock or not. You'd have to call orig. service company on that one.
____________________ I Don't know yet! |
||||||||||||||
| |||||||||||||||
| Current time is 10:44 pm
|
Page: 1 2 3 |
| ApplianceGuru.com: The Samurai Appliance Repair Forums > Do-It-Yourself Appliance Repair Help > The Kitchen Appliance Repair Forum > subzero refrigerator 561 cold at bottom warm at top | Top |
| Find Appliance Parts & Diagrams Here |
| Enter a model number, part number, type of appliance, brand, or even a part description. |
|
365-day return policy on all parts ordered through this site! |
FAQs | Contact | Apprenticeship | Consultations | Parts | Model Number Help | Newsletter | Beer | Fixitnow.com