Basic Troubleshooting of Electric Heat  Rate Topic 
AuthorPost
 Posted: Wed Feb 4th, 2009 05:07 pm
  PM Quote Reply
1st Post
Bobice

 

Joined: Sun Nov 30th, 2008
Location: Bay Shore, New York USA
Posts: 194
Flavorite Brew: Coffee
Status: 
Offline

ELECTRIC HEATING TROUBLESHOOTING CHART[size=] Problem Possible cause Solution Furnace won't run 1. No power. 1. Check for blown fuses or tripped
circuit breakers at main entrance
panel, at separate entrance panel,
and on or in furnace; restore circuit.   2. Switch off. 2. Turn on separate power switch
on or near furnace.   3. Motor overload. 3. Wait 30 minutes; press reset
button. Repeat if necessary. Not enough heat 1. Thermostat set
too low. 1. Raise thermostat setting 5°.   2. Filter dirty. 2. Clean or replace filter.   3. Blower clogged. 3. Clean blower assembly.   4. Registers closed
or blocked. 4. Make sure all registers are open;
make sure they are not blocked
by rugs, drapes, or furniture.   5. System out of
balance. 5. Balance system.   6. Blower belt loose
or broken. 6. Adjust or replace belt.   7. Element faulty. 7.Replace element. Furnace turns
on and off
repeatedly 1. Filter dirty.
2. Motor and/or
blower needs 1. Clean or replace filter.
2. If motor and blower have oil
ports, lubricate.   lubrication.     3. Blower clogged. 3. Clean blower assembly. Blower won't
stop running 1. Blower control
set wrong. 1. Reset thermostat from ON
to AUTO.   2. Relays faulty. 2.Replace relay. Furnace noisy 1. Access panels
loose. 1. Mount and fasten access
panels correctly.   2. Belts sticking, worn,
or damaged. 2. Spray squeaking belts with
fan belt dressing; replace worn
or damaged belts.   3. Blower belt too
loose or too tight. 3. Adjust belt.   4. Motor and/or blower
needs lubrication. 4. If motor and blower have oil
ports, lubricate.       Problem: Electric heat will not come on or fan will not come on. 1. First and most important, Please make sure your electrical power is turned off before trying to repair or inspect any type of electrical appliance. I would recommend that you purchase a Multi Meter for some of the troubleshooting procedures listed. 2. Inspect the inside of the air handler or electric furnace for burnt wires. I find this to be a major problem. Electric furnaces use lots of electricity. Any connections that are the least bit loose inside the furnace will cause a heat build up, arcing and eventually a completely burned off connection. Before long the entire wire will be burnt off. Please see picture (compliments from one of our nice customers) below of a burnt heat sequencer. You can see where the heat build up and arcing has caused the terminals to completely burn off the left side! This looks like a three stack sequencer, because of the divisions in the layers of the sequencer:
3. Check your breakers or fuses inside the air handler. Again, make sure your power is off. A good multimeter would be nice to test your fuses. ·        Set the meter to the Rx1 scale (horseshoe), place one lead on each end of fuse. If the fuse is good, you should read zero. If the fuse is bad, you should read infinity (no reading at all).     4. If you still are not getting electric heat then you should test your sequencers to make sure they are working. You can make yourself a tester so you could get portable 24 volts without having the furnace power turned on by using a fan center connected to a junction box.

 

When 24 volts is applied across the two bottom connections (coil) on most sequencers, you should get continuity (a closed circuit) between the two terminals the one on the left M1 and the one on the right M2. You should also have continuity between M3 & M4. This might take 30 to 90 seconds after the 24 volts is applied before you get the continuity. If you do not get continuity then, the sequencer is no good.

 

 
What do we check if our electric heat is not working? There are a few basic things to check yourself. Other steps require an expert.
    Is the thermostat asking for heat? Be sure you know where all of the thermostats for your electric heat are located. Some heaters such as flush-in-floor electric heaters may use a wall-mounted thermostat while other electric baseboard heaters may have individual thermostats on each baseboard unit. In a bathroom with electric radiant heat in the floor, Is electrical power on to the heater? Check the fuses or circuit breakers that supply each electric heater. If the electric furnace does not seem to be making heat, the electrician or heating technician will use an ammeter to test each of the heating elements to see if one or more of them is not working. She will also check first to confirm that electrical power is on to the unit. If one or more of the staged electric heaters in the furnace has failed, the furnace may make warm air, but not enough warm air in very cold conditions. Check the air temperature rise across the electric furnace. When the furnace has been operating for 20 minutes or longer, typically the temperature at the return plenum (the lower thermometer in the sketch) will show about 70 deg .F. and the supply plenum temperature will be between 120 deg .f. and 125 deg .f. If the supply plenum temperature is too high (over130 deg .f.) something's wrong and you should call a heating service technician. Check radiant heat ceiling panels for wire interruptions. If someone drove an nail into a radiant panel or in the attic above they damaged a wire or heating panel, you may find that that room no longer has heat. We use a hand-held infra-red thermometer scanner to quickly check radiant heat floors and ceilings.
The following is for experienced technicians.
 
    Does the fan start up even with the fan lead removed from the thermostat ?  A grounded heater coil can cause this to happen. 



____________________
Retired US Army Refrigeration Specialist / NYC Board of Education HVAC/R (Retired)
40 Years HVAC/R service, sales,installations. a tragedy has happen to me : http://web.me.com/zenzoidman/Bobice/
Back To Top PM Quote Reply  

 Posted: Fri Feb 6th, 2009 02:22 am
  PM Quote Reply
2nd Post
applianceman18007260692
Fellow, Academy of Sublime Masters of Appliantology


Joined: Thu Nov 17th, 2005
Location: Mobile, Alabama USA
Posts: 1119
Flavorite Brew: Keystone Light
Status: 
Offline
Electric Heat How does electric heat work? Having a basic understanding of what is happening greatly increases your ability to diagnose and repair these heaters. All of them basically work the same. Just as an air conditioner A-coil needs a certain amount of freon flowing through it, Air must be traveling over the heating coils at a certain rate or they will simply heat up and disentergrate in a very short time. But if the fan comes on straight away then only cold air will come out of the vent!. So how do they do it? The manufacturer installs a sequencer to bring on the heating coils in stages.   Typical sequencer with 4 stages   This does 2 things. Pre warms the heater and keeps the breaker from tripping. A heating coil is first brought on to heat up the furnace and then 30 seconds later another one comes on 30 seconds later the fan and another one kicks in. Each coil is approximitly 5000 watts the typical furnace for a 3 bedroom. These coils will break individually and instead of 15000 watts you have 10000 or even 5000. Many times people would bring the heat strip to me with all 3 coils broken. Can you imagine that? The good news is each coil can be restrung
     typical restring kit   and the heater can be brought back up to normal. When restringing any element you must have the coils evenly spaced and you cannot have any gaps or they become weak spots and burn out. You must take care not to let the coil touch the heater chamber also.  



____________________
"May the hinges of our friendship never grow rusty"
-old Irish saying

Buy me a Beer: http://web.me.com/zenzoidman/applianceman18007260692/
Back To Top PM Quote Reply

 Posted: Fri Feb 6th, 2009 01:50 pm
  PM Quote Reply
3rd Post
Bobice

 

Joined: Sun Nov 30th, 2008
Location: Bay Shore, New York USA
Posts: 194
Flavorite Brew: Coffee
Status: 
Offline
Thanks for the photos JW :D



____________________
Retired US Army Refrigeration Specialist / NYC Board of Education HVAC/R (Retired)
40 Years HVAC/R service, sales,installations. a tragedy has happen to me : http://web.me.com/zenzoidman/Bobice/
Back To Top PM Quote Reply  

 Posted: Mon Feb 9th, 2009 02:50 am
  PM Quote Reply
4th Post
Samurai Appliance Repair Man
Fermented Grand Master of Appliantology


Joined: Mon Mar 21st, 2005
Location: Otterville, New Hampshire USA
Posts: 16082
Flavorite Brew: Kirin Ichiban
Status: 
Offline
Bobice wrote: Thanks for the photos JW :D

Them's good'ns!  Verlly helpful post, too, Bobice.  Domo!



____________________
To ask a question, use our new forums==> http://appliantology.org

365-Day No-Hassle Return Policy on all parts purchased through this site, even electrical parts that have been installed!
Back To Top PM Quote Reply

 Posted: Fri Apr 17th, 2009 04:50 am
  PM Quote Reply
5th Post
helowrench
Merit Apprentice Appliantologist
 

Joined: Thu Nov 30th, 2006
Location: Dallas, Texas USA
Posts: 7
Flavorite Brew: Killian's Red
Status: 
Offline
Maintaining the all electric house, I have to deal with a 30 year old furnace. I have gone to using tricks and tips from the aviation world the keep things flying right.
When I decided to install all new wiring due to 1 or 2 wires blowing out every single year, first I sourced wire that was correctly rated, and as I cut each individual wire, I coated each end with a film of DOW compound #4 then installed properly rated crimp connects, coated them with DOW4 then installed onto the proper connections.
The DOW4 is a silicone compound that is non drying, and will prevent the corrosion that leads to the high resistance areas that heat up when power is applied, and blow apart the wire.
Since I did this I have had 4 years of trouble free operation, which is much better than awakening at 3 AM to find the beer freezing in the fridge with a temp inside the house of 45 and having to fix the heater (in the garage) with a garage temp of 15.
I use DOW 4 on all of my electrical connections, no matter what they are, since it helps by keeping voltages stable by keeping humidity from causing corrosion.



____________________
These are my tools. There are many like them, but these are mine. My tools are my best friends, they are my life. I must master them as I master my life. Without me my tools are useless. Without them I am useless. I must use my tools true.
Back To Top PM Quote Reply  

 Posted: Sat Apr 18th, 2009 06:45 am
  PM Quote Reply
6th Post
grey one



Joined: Sat Mar 7th, 2009
Location: Cobble Hill, British Columbia Canada
Posts: 345
Flavorite Brew: havana club rum
Status: 
Offline
Thanks for the info guys. Since semi-retiring here 1.5 yrs. ago , I have been up close and personal with my 15 yr. old furnace twice :1 fuse and 1 relay and also my neighbors for a relay. Did not fully understand operation  - so thanks again..

Back To Top PM Quote Reply

 Posted: Sat Apr 18th, 2009 03:15 pm
  PM Quote Reply
7th Post
Bobice

 

Joined: Sun Nov 30th, 2008
Location: Bay Shore, New York USA
Posts: 194
Flavorite Brew: Coffee
Status: 
Offline
I love to help as many people as I can. In these tough economic times I believe everyone appreciates it and knows when their limit is reached and call in a professional.
I also try and educate as there are too many "Salesmechanics".
Funny I am at this over forty years and never had to sell people repairs they did not need to stay around.



____________________
Retired US Army Refrigeration Specialist / NYC Board of Education HVAC/R (Retired)
40 Years HVAC/R service, sales,installations. a tragedy has happen to me : http://web.me.com/zenzoidman/Bobice/
Back To Top PM Quote Reply  

Current time is 06:54 am Tell a friend about this page... all your other friends are doing it!  
- > Do-It-Yourself Appliance Repair Help > Heating, Ventilation, and Air Conditioning (HVAC) > Basic Troubleshooting of Electric Heat Top



Find Appliance Parts & Diagrams Here
Enter a model number, part number, type of appliance, brand, or even a part description.

365-day return policy on all parts ordered through this site!

FAQs | Contact | Apprenticeship | Parts | Model Number Help | Newsletter | Beer

Your Sometimes-Lucid Host:
- Home
"If I can't help you fix your appliance and make you 100% satisfied, I will come to your home and slice open my belly, spilling my steaming entrails onto your floor."


UltraBB 1.17 Copyright © 2007-2008 Data 1 Systems
Page processed in 0.0934 seconds (8% database + 92% PHP). 27 queries executed.

Web Analytics