| Bard Wall Mounted A/C Model WA372-A10 Package EHWA03-A10 | Rate Topic |
| Author | Post |
|---|
| Posted: Mon Jun 21st, 2010 05:13 pm |
|
1st Post |
|
papollonia Senior Apprentice Appliantologist
|
Hey Guys: I work at my kids school as General Maintenance. We have 5 modular building. Each has about 10 Bard Wall Mounted A/C Model WA372-A10 Package EHWA03-A10 Units. I am stumped on this one!! One of the Modular building, the A/C was working on Friday when i left. I come in today and none of them are working. Checked the Following: The power switch on each unit (was on) Checked the circuit breaker (flipped it back and forth) it is 'On' Check T-Stat - Set to 75degree, temp in rooms about 88 degree. T-Stat is set to a/c. ANy Ideas here? I have a feeling i am missing something that is right in front of my face!! Thanks
|
||||||||||||||
| |||||||||||||||
| Posted: Mon Jun 21st, 2010 05:27 pm |
|
2nd Post |
|
RegUS_PatOff Fellow, Academy of Sublime Masters of Appliantology
|
papollonia wrote: ... I have a feeling i am missing something that is right in front of my face!! Is there some type of "Timer" that shuts off the Systems at the end of the school year ?
____________________ The new repair forums==> http://appliantology.org RegUS_PatOff http://www.youtube.com/watch?v=oPAY2LsKVEw my video production: “Easter Seals Walk With Me” http://www.youtube.com/watch?v=-EBiLyYXMiA |
|||||||||||||
| ||||||||||||||
| Posted: Mon Jun 21st, 2010 06:43 pm |
|
3rd Post |
|
papollonia Senior Apprentice Appliantologist
|
Thank you for replying. Not that I know of.
|
||||||||||||||
| |||||||||||||||
| Posted: Sun Aug 29th, 2010 03:42 am |
|
4th Post |
dkpd1581
|
Verify 208/230 VAC to transformer. Verify transformer is tapped for correct incoming voltage. Transformers set at 230 VAC tap but being supplied with only 208 VAC will not produce a LV signal of at least 22 VAC to run LV system. Retap as necessary. Check to see if there is 24 VAC coming out of the transformer - if not find reason why the high side windings are open or 3-5 amp fuse is blown. If 24 VAC is coming out of the transformer and through the 3-5 amp circuit, follow it through the LV circuits - going into board and not out is possible bad board. Out of board but not to contactor - possible limit switch open (HP manual reset, LP auto reset defective). No board - follow through relay coils - coils open replace relay. Coils good but contacts do not change state - replace relay. 24 VAC to contactor coil of compressor and/or fan contactor relay but no change of state in contacts same as above. If contacts change state but full voltage registered across closed contacts means the contact surface is bad or obstructed. Clean contacts or replace as necessary. 24 VAC circuit is closed and completing a proper path, contactors change state, and zero voltage is registered across closed contacts, check OL switch on compressor, check physical connections in HV circuit, compressor windings for shorts to ground, partially shorted windings, open windings. If compressor tries to start but is unable to, pulls locked rotor amps and quits, check the capacitor and verify that its within 10 percent of name plate value - if not replace. If all else is good install a hard start capacitor. If compressor tries and fails to start with all the above, you may have a physically locked up compressor and a last effort is to strike the compressor head on start up in an attempt to dislodge the seizure. Try this and let us know what happens.
____________________ |
|||||||||||||
| ||||||||||||||
| Posted: Wed Sep 1st, 2010 01:55 am |
|
5th Post |
AmTec Services
|
If all are not working (5?) it seems you need to look for a common link. Timers,energy managment devices, or fire alarm circuits are all suspect when you have multi nothing runs problem. Look for the common link. ........................AmTec
____________________ The futures so bright, I gotta wear shades! |
||||||||||||||
| |||||||||||||||
| Posted: Wed Sep 1st, 2010 06:23 pm |
|
6th Post |
|
applianceman18007260692 Fellow, Academy of Sublime Masters of Appliantology
|
All 5 units are out at once? Sabotage!
____________________ "May the hinges of our friendship never grow rusty" -old Irish saying Buy me a Beer: http://web.me.com/zenzoidman/applianceman18007260692/ |
|||||||||||||
| ||||||||||||||
| Current time is 10:36 pm
|
|
| ApplianceGuru.com: The Samurai Appliance Repair Forums > Do-It-Yourself Appliance Repair Help > Heating, Ventilation, and Air Conditioning (HVAC) > Bard Wall Mounted A/C Model WA372-A10 Package EHWA03-A10 | Top |
| Find Appliance Parts & Diagrams Here |
| Enter a model number, part number, type of appliance, brand, or even a part description. |
|
365-day return policy on all parts ordered through this site! |
FAQs | Contact | Apprenticeship | Consultations | Parts | Model Number Help | Newsletter | Beer | Fixitnow.com