| Getting a Code 31 Error on Furnace model No. GB3AAV | Rate Topic |
| Author | Post |
|---|
| Posted: Thu Dec 11th, 2008 10:42 pm |
|
1st Post |
|
ccmulder Senior Apprentice Appliantologist
|
Okay--I checed the blinking LCD and get a Code 31 Error, which says to check for a number of things but I think its this: Defective Pressure swith or connections. The reason I say that is because right after that, it says, "If it opens after trial for ignition period, blower will come on for 90 second recycle delay." Now that's what happens with mine. If I reset the door switch (i.e., just push in the switch that would be pushed in if you put the service access door back on), the heater comes on for 90 seconds and then shuts off. This problem was intermittent for a couple days--the heater would come on later at night, but now doesn't come on at all. Is there any way to check for that/fix? If I need it a repair, what should it cost? Attached is a picture--which is the Pressure Switch? Attachment: heater.jpg (Downloaded 41 times)
|
||||||||||||||
| |||||||||||||||
| Posted: Thu Dec 11th, 2008 10:45 pm |
|
2nd Post |
|
ccmulder Senior Apprentice Appliantologist
|
Here is a closer shot Attachment: heater2.jpg (Downloaded 40 times)
|
|||||||||||||
| ||||||||||||||
| Posted: Thu Dec 11th, 2008 10:49 pm |
|
3rd Post |
|
RegUS_PatOff Fellow, Academy of Sublime Masters of Appliantology
|
I'm no expert, but it looks like that round blue diaphram thing in the second picture. Last edited on Thu Dec 11th, 2008 10:50 pm by RegUS_PatOff ____________________ RegUS_PatOff http://www.youtube.com/watch?v=oPAY2LsKVEw my video production: “Easter Seals Walk With Me” (also in HQ) http://www.youtube.com/watch?v=-EBiLyYXMiA Upon leaving this Earth "Do you want the Smoking or Non-Smoking section ?" |
||||||||||||||
| |||||||||||||||
| Posted: Thu Dec 11th, 2008 10:53 pm |
|
4th Post |
|
ccmulder Senior Apprentice Appliantologist
|
RegUS_PatOff wrote: I'm no expert, but it looks like that round blue thing in the second picture. That's what I thought--but its confusing--you can see on the attached diagram from the service manual (mine is the one on the right, but horizontal): Attachment: Diagram.jpg (Downloaded 40 times) Last edited on Thu Dec 11th, 2008 10:53 pm by ccmulder |
|||||||||||||
| ||||||||||||||
| Posted: Thu Dec 11th, 2008 11:25 pm |
|
5th Post |
|
RegUS_PatOff Fellow, Academy of Sublime Masters of Appliantology
|
http://www.amresupply.com/product/HK06WC090 http://www.hvacpartsoutlet.com/pressureswitchcarrierhk06wc090.aspx "NOTE; the new pressure switch may look and mount differently then the old switch it replaces. The connection terminals may also have to be changed, --in some cases you may even need to make a new mounting bracket from a small piece of sheet metal *not included, or change the wire connectors." Check the Vent to see if there's any restrictions, i.e. critters..... Last edited on Thu Dec 11th, 2008 11:31 pm by RegUS_PatOff ____________________ RegUS_PatOff http://www.youtube.com/watch?v=oPAY2LsKVEw my video production: “Easter Seals Walk With Me” (also in HQ) http://www.youtube.com/watch?v=-EBiLyYXMiA Upon leaving this Earth "Do you want the Smoking or Non-Smoking section ?" |
||||||||||||||
| |||||||||||||||
| Posted: Thu Dec 11th, 2008 11:35 pm |
|
6th Post |
|
ccmulder Senior Apprentice Appliantologist
|
Where would the vent be?
|
|||||||||||||
| ||||||||||||||
| Posted: Thu Dec 11th, 2008 11:45 pm |
|
7th Post |
|
ccmulder Senior Apprentice Appliantologist
|
RegUS_PatOff wrote: http://www.amresupply.com/product/HK06WC090 Thanks for the link although I don't know if its the pressure switch. Any way to check that?
|
||||||||||||||
| |||||||||||||||
| Posted: Thu Dec 11th, 2008 11:58 pm |
|
8th Post |
|
RegUS_PatOff Fellow, Academy of Sublime Masters of Appliantology
|
ccmulder wrote: Where would the vent be?the metal vent pipe that goes thru the wall, or up the chimney... Last edited on Thu Dec 11th, 2008 11:59 pm by RegUS_PatOff ____________________ RegUS_PatOff http://www.youtube.com/watch?v=oPAY2LsKVEw my video production: “Easter Seals Walk With Me” (also in HQ) http://www.youtube.com/watch?v=-EBiLyYXMiA Upon leaving this Earth "Do you want the Smoking or Non-Smoking section ?" |
|||||||||||||
| ||||||||||||||
| Posted: Fri Dec 12th, 2008 01:40 am |
|
9th Post |
|
ccmulder Senior Apprentice Appliantologist
|
RegUS_PatOff wrote: ccmulder wrote:Where would the vent be?the metal vent pipe that goes thru the wall, or up the chimney... Ok--I'll check tomorrow in daylight. However, I jumpered the Pressure Switch and then I got a 23 code error (Pressure switch did not open) which I'm guessing unless the unit senses a pressure switch opening, it faults. But I guess that still doesn't tell me if the pressure switch is working properly or not if something else is wrong. I know the switch comes opens after trial for ignition because the blower runs for 90 seconds and shuts off.
|
||||||||||||||
| |||||||||||||||
| Posted: Fri Dec 12th, 2008 07:57 am |
|
10th Post |
|
ROBBYRIG Sublime Master of Appliantology
|
Jumpering a pressure switch is different than jumpering other switches. At initial start-up, the board needs to read the pressure switch as open. After the inducer motor kicks on for a minute or so, then the pressure switch closes and the board will then allow the ignitor to glow.
|
|||||||||||||
| ||||||||||||||
| Posted: Fri Dec 12th, 2008 12:37 pm |
|
11th Post |
|
ccmulder Senior Apprentice Appliantologist
|
ROBBYRIG wrote: Jumpering a pressure switch is different than jumpering other switches. At initial start-up, the board needs to read the pressure switch as open. After the inducer motor kicks on for a minute or so, then the pressure switch closes and the board will then allow the ignitor to glow. Is there anyway to test the switch? Also, how do I check the vent? I don't know how to take apart the aluminum piping that goes from the unit to the roof--tried last night, but it doesn't just pull apart
|
||||||||||||||
| |||||||||||||||
| Posted: Sat Dec 13th, 2008 03:58 pm |
|
12th Post |
|
applianceman18007260692 Sublime Master of Appliantology
|
You probably need to blow out that rubber tube. The way to check the pressure switch is to suck on it. You should hear an audible click. Check for continuity. The way it works is the draft indcer motor causes suction and the suction kicks the pressure switch on which activates the ignition sequence. The ignitor comes on and the gas fires up, the flame sensor says everything is fired up and the heater warms up then the blower kicks on. NOTE: if the flame sensor does not confirm ignition because it is contaminated or the burner ground wire is loose then you will have the symtoms you have described. The main fan will do the 90 second thing just in case ignition did occur but the brain didn't get the word. You could try cleaning the sensor with soft emeory cloth or just replace it. Make sure all ground wires have good connections. Last edited on Sat Dec 13th, 2008 04:00 pm by applianceman18007260692 ____________________ "May the hinges of our friendship never grow rusty" Old Irish Saying |
|||||||||||||
| ||||||||||||||
| Posted: Sat Dec 13th, 2008 04:05 pm |
|
13th Post |
|
ccmulder Senior Apprentice Appliantologist
|
I did take the pressure switch off and sucked on it and heard the clicking sound so I assume that means it works.
|
||||||||||||||
| |||||||||||||||
| Posted: Sat Dec 13th, 2008 04:45 pm |
|
14th Post |
|
applianceman18007260692 Sublime Master of Appliantology
|
I have never seen a bad one yet. I worked at an HVAC parts store since 1995. Most of the time it is a blocled hose. bad draft blower or faulty flame sensor.
____________________ "May the hinges of our friendship never grow rusty" Old Irish Saying |
|||||||||||||
| ||||||||||||||
| Posted: Sat Dec 13th, 2008 04:46 pm |
|
15th Post |
|
applianceman18007260692 Sublime Master of Appliantology
|
I sure wish I knew why I can't type worth a damn today.
____________________ "May the hinges of our friendship never grow rusty" Old Irish Saying |
||||||||||||||
| |||||||||||||||
| Posted: Sat Dec 13th, 2008 06:02 pm |
|
16th Post |
|
ccmulder Senior Apprentice Appliantologist
|
applianceman18007260692 wrote: I have never seen a bad one yet. I worked at an HVAC parts store since 1995. Most of the time it is a blocled hose. bad draft blower or faulty flame sensor. Okay--I had a guy come out and troubleshoot it--he says its a bad master controller board (or inducer board). Interestingly, he showed me that if I pressed up on the controller board with my fingers, it would make the system work. So apparently I can stand their with my hand on the controller board or clamp it somehow or order a new one. Any ideas on what may be wrong with the board or should I just order a new one? Last edited on Sat Dec 13th, 2008 07:11 pm by ccmulder |
|||||||||||||
| ||||||||||||||
| Posted: Sat Dec 13th, 2008 07:22 pm |
|
17th Post |
|
RegUS_PatOff Fellow, Academy of Sublime Masters of Appliantology
|
ccmulder wrote: ... if I pressed up on the controller board with my fingers, it would make the system work.... ... Any ideas on what may be wrong with the board or should I just order a new one? bad solder joint, maybe on a Connector or Relay Terminal ... Take a close look ...
____________________ RegUS_PatOff http://www.youtube.com/watch?v=oPAY2LsKVEw my video production: “Easter Seals Walk With Me” (also in HQ) http://www.youtube.com/watch?v=-EBiLyYXMiA Upon leaving this Earth "Do you want the Smoking or Non-Smoking section ?" |
||||||||||||||
| |||||||||||||||
| Posted: Sat Dec 13th, 2008 08:27 pm |
|
18th Post |
|
ccmulder Senior Apprentice Appliantologist
|
RegUS_PatOff wrote: ccmulder wrote:... if I pressed up on the controller board with my fingers, it would make the system work.... ... Any ideas on what may be wrong with the board or should I just order a new one? Yeah--that's obviously it--a bad connection--but with a 13 year old heater, I thought its probably a better idea to just replace the board with a new one. I didn't see any Model Number on the board though--how would I find a replacement?
|
|||||||||||||
| ||||||||||||||
| Posted: Sat Dec 13th, 2008 08:42 pm |
|
19th Post |
|
RegUS_PatOff Fellow, Academy of Sublime Masters of Appliantology
|
http://shortyshvac.com/index.php?main_page=product_info&products_id=39 325878-751 This board replaces HK42FZ004 CARRIER BOARDS 325878* on eBay Last edited on Sat Dec 13th, 2008 08:45 pm by RegUS_PatOff ____________________ RegUS_PatOff http://www.youtube.com/watch?v=oPAY2LsKVEw my video production: “Easter Seals Walk With Me” (also in HQ) http://www.youtube.com/watch?v=-EBiLyYXMiA Upon leaving this Earth "Do you want the Smoking or Non-Smoking section ?" |
||||||||||||||
| |||||||||||||||
| Posted: Sat Dec 13th, 2008 08:51 pm |
|
20th Post |
|
ccmulder Senior Apprentice Appliantologist
|
RegUS_PatOff wrote: http://shortyshvac.com/index.php?main_page=product_info&products_id=39 I saw those when I searched but I was unsure which model it replaces They list HK42FZ0xx where "xx" are 08 07 or 11 or 13 or 16. Does it matter which one I get or are the all the same?
|
|||||||||||||
| ||||||||||||||